The same happened to me.
There were some constructions assigned to shading elements and adjacent buildings that were coming up in the report.
I changed them all to constructions that are actually used in the building I am analysing.
In this way they are removed from the report as well, but:
1 ...
Search found 3 matches
- Thu Oct 15, 2015 9:36 am
- Forum: ASHRAE 90.1 App. G - PRM
- Topic: BPRM Report
- Replies: 3
- Views: 26160
- Mon Oct 12, 2015 12:05 pm
- Forum: ASHRAE 90.1 App. G - PRM
- Topic: PRM - Fan power calculation
- Replies: 2
- Views: 15430
Re: PRM - Fan power calculation
I have noticed the same thing.
For a baseline system type 7 with a fan supply flowrate of 19698.96cfm and a pressure drop adjustment of 4 in. w.c., IES gives a fan power of 23.9kW.
Manually applying the ASHRAE calculation I get 35.8kW.
It is quite a significant difference!
Has anyone found the ...
For a baseline system type 7 with a fan supply flowrate of 19698.96cfm and a pressure drop adjustment of 4 in. w.c., IES gives a fan power of 23.9kW.
Manually applying the ASHRAE calculation I get 35.8kW.
It is quite a significant difference!
Has anyone found the ...
- Sun Oct 11, 2015 11:58 am
- Forum: ASHRAE 90.1 App. G - PRM
- Topic: PRM Sizing reports bug?
- Replies: 1
- Views: 14087
PRM Sizing reports bug?
I noticed that the Airflows section in the sizing reports for both the baseline and proposed systems is not populated. It shows 0 l/s in all room and the %OA at the AHU level is 0% as well.
All OA flowrates and exhaust air flowrates are correctly set in all Loads spreadsheet and in the system file ...
All OA flowrates and exhaust air flowrates are correctly set in all Loads spreadsheet and in the system file ...