Search found 3 matches

by FrancescoMI
Fri Aug 31, 2018 10:23 am
Forum: ApacheHVAC
Topic: VAV Reheat with Radiant Panels (Sequence)
Replies: 2
Views: 14776

Re: VAV Reheat with Radiant Panels (Sequence)

I would use a little bit different setpoint temperatures.
Suppose that the setpoint temperature for the radiant panels is 20°C. You can use 19.5°C as setpoint temperature for the VAV reheat coil. The VAV reheat coil will work only if the radiant system is not able to meet the 20°C setpoint ...
by FrancescoMI
Thu Aug 30, 2018 3:23 pm
Forum: ApacheHVAC
Topic: IPLV for chillers
Replies: 0
Views: 79793

IPLV for chillers

I'm modeling a baseline model for ASHRAE 90.1-2007. The chiller efficiency has to respect Table 6.8.1C for screw chillers.
Suppose that the autosized cooling power for every chiller is 600 kW (2 chillers).
The efficiency should be 4.90 COP and 5.60 IPLV.
How can I be sure that the IPLV is respected ...
by FrancescoMI
Thu Aug 30, 2018 3:22 pm
Forum: ApacheHVAC
Topic: IPLV for chillers
Replies: 0
Views: 79553

IPLV for chillers

I'm modeling a baseline model for ASHRAE 90.1-2007. The chiller efficiency has to respect Table 6.8.1C for screw chillers.
Suppose that the autosized cooling power for every chiller is 600 kW (2 chillers).
The efficiency should be 4.90 COP and 5.60 IPLV.
How can I be sure that the IPLV is respected ...