Thanks for your help.....however, I found that the issue was caused by an extremely high Notional Alpha value (over 1000%!!!).
By running the Compliance on individual rooms I worked out that 3no adjacent rooms were causing the problem.
I deleted them and re-modelled them (exactly the same as I did ...
Search found 2 matches
- Tue Nov 19, 2013 11:49 am
- Forum: Part L2 - England & Wales
- Topic: Odd Looking TER ob SBEM Compliance
- Replies: 2
- Views: 15444
- Mon Nov 18, 2013 3:27 pm
- Forum: Part L2 - England & Wales
- Topic: Odd Looking TER ob SBEM Compliance
- Replies: 2
- Views: 15444
Odd Looking TER ob SBEM Compliance
Hello,
I have just completed modelling a small school block (approx 470m2) using 100% building area as D1 Primary School.
When I have run the SBEM Compliance calculation the TER is being calculated as 105.6 and the BER is 29.3.
When I have looked at the BRUKL Output Document the heating energy ...
I have just completed modelling a small school block (approx 470m2) using 100% building area as D1 Primary School.
When I have run the SBEM Compliance calculation the TER is being calculated as 105.6 and the BER is 29.3.
When I have looked at the BRUKL Output Document the heating energy ...