Criterion 3 and transient spaces

Part L2 of the Building Regulations (2006 edition).
Post Reply
bootsam
VE Professor
VE Professor
Posts: 184
Joined: Fri Sep 10, 2010 1:15 pm

Criterion 3 and transient spaces

Post by bootsam »

Ive a transient space. Defined as a circulation area. According to Para4.44d of Part L2A these should be excluded. However it is still assessing the space and failing it. Its a foyer/lobby with a glazed part of its roof. This area should not be being considered amongst the checks. Whassup?

??
User avatar
Terence
Site Admin
Site Admin
Posts: 412
Joined: Mon Aug 25, 2008 12:58 pm
Location: Glasgow, UK
Contact:

Re: Criterion 3 and transient spaces

Post by Terence »

Is the space cooled? In accordance with the 2010 NCM modelling guide, ApacheSim Compliance only performs Criterion 3 check on applicable rooms, i.e it will only report results for rooms that are occupied or mechanically cooled.
Terence McMahon
IES Technical Support
Linkedin