SHGC and Total Shading Coefficient

Post Reply
myope
VE Beginner
VE Beginner
Posts: 23
Joined: Thu Jun 16, 2011 8:42 am

SHGC and Total Shading Coefficient

Post by myope »

In construction I see Total Coefficient for glazing after deriving parameter, in general or theory, SHGC = SC x 0.87. So total Coefficient in VE equivalent SHGC or SC ?

Thanks.
User avatar
Terence
Site Admin
Site Admin
Posts: 412
Joined: Mon Aug 25, 2008 12:58 pm
Location: Glasgow, UK
Contact:

Re: SHGC and Total Shading Coefficient

Post by Terence »

The SHGC is calculated as follows:

SHGC = Total shading coefficient * 0.87

This complies with NFRC. If you wish to view the calculated SHGC then you can do so by switching the U-Value method to ASHRAE, you’ll then be able to view the SHGC in derived parameters.
Terence McMahon
IES Technical Support